Re: Gas pipe bonding
Gentlemen,
I have a current copy the NFGC-NFPA-44-2002 Edition.
Article 8.6.1 Electrical Connections:
Electrical connections between gas utilization equipment and the building wiring, including the grounding of the equipment, shall conform, to NFPA 70 NEC.
Article 8.6.4 Continuous Power:
All gas utilization equipment using electrical controls shall have the controls connected into a permanently live electric circuit --that is, one that is not controlled by a light switch. Central heating equipment shall be provided with a separate electrical circuit.
The following commentary was taken from the NFGC NFPA-54-2002 Handbook:
"The National Electrical Code requires a separate electrical circuit and over current protection for central heating equipment, as well as a means for disconnecting the power source at or within sight from the appliance. This separate circuit also can include circulating water pumps, valves, humidifiers, electronic air cleaners, and other accessories normally associated with the equipment. Certain appliances and installations also are permitted to be connected with a flexible cord that has a grounding-type attachment plug. The grounding-type attachment plug also serves as a disconnecting means for future service & maintenance. In subsection 8.6.4, note the phrase "a permanently live electrical circuit --that is, one that is not controlled by a light switch." This requirement thus prohibits "emergency shutoff" switches. In areas where oil is a common source of heating fuel, wall switches with red cover plates marked "Oil Burner Emergency Switch" are installed in buildings heated by fuel oil, as required by NFPA-31, Standard for the Installation of Oil-Burning Equipment, to stop the flow of oil to the burner. When converting an oil furnace or boiler to gas, the emergency switch must be removed. Emergency switches must not be installed when installing a new gas boiler. The emergency shutoff switch provides safety for oil-fired heating equipment, because failure of the boiler or furnace to shut off can prevent the oil pump from shutting off, thereby filling the equipment and surrounding area with oil. An oil pool fire is possibile. With gas-fuelded equipment, the emergency shutoff valve required in subsection 6.9.3 provides equivalent safety.
I don't know about you guys, but I always install an emergency shutoff switch with the appropriate indicating cover plate. I guess this is a voilation? Maybe the arcing of a shutoff switch could ignite a gas mixture, but then again, most people will turn on the basement light first. Additionally, I have numerous rooftop Gas Fired HVAC units that all have disconnects, how can this be a violation. The emergency switch does not interrupt or break the grounding & bonding. This subject definitely needs some clarification
[ April 19, 2004, 01:39 PM: Message edited by: sbe ]