All are limited to a maximum of 122 degrees F ambient temperature...in the USA.
I pretty sure RTRC would work great. RTRC is just geek speak for fiberglass reinforced epoxy, or just fiberglass conduit. No expected sag, though it may just a tad over time and exposure.Do you know if there is any other non-metallic conduit type, that is more suitable for installing outdoors in sunlight, in applications such as this?...
I pretty sure RTRC would work great. RTRC is just geek speak for fiberglass reinforced epoxy, or just fiberglass conduit. No expected sag, though it may just a tad over time and exposure.
Now obtaining, pricing, and installation are all a bit more challenging than PVC.
50?C ambient temperature, same restriction as PVC [352.12(D)].355.12(D) has the 122 degree F temp limitation...
1.2 The products specified in this Standard are intended for use at -40?C (-40?F) to 110 ?C (230?F). The products are for use above ground in exposed and concealed locations. The products are also suitable for use below ground by direct burial or by encasement in concrete.
1.2.3 The following restrictions apply to use of the Schedule 40 and Schedule 80 rigid PVC conduit and fittings mentioned in 1.1.1:
a) Use at 50?C (122?F) and lower ambient temperatures and
b) Use with 75?C (167?F) wiring, but the conduit and fittings may be used with 90?C (194?F) wiring if they comply with the construction (see Conduit for Use with 90?C Wire, 6.15) and marking (see 8.2.1, 8.2.4 and 8.2.5) requirements covering use with 90?C (194?F) wiring.
Do you know if there is any other non-metallic conduit type, that is more suitable for installing outdoors in sunlight, in applications such as this?
It certainly helps to not need to think about grounding.