This is the panel action from the ROC on the proposed smoke detector exemption from the AFCI requirement.
______________________________________________________________
2-107 Log #1335 NEC-P02 Final Action: Reject
( 210.12(B) Exception (New) )
________________________________________________________________
Submitter: Joseph A. Ross, Ross Seminars
Comment on Proposal No: 2-134a
Recommendation: Add a new Exception No. 3 as follows:
Exception No. 3: AFCI protection shall not be required for permanently installed alarm systems (fire, smoke, and burglar) in dwelling units.
Substantiation: The submitter agrees with the new additions of Exceptions Nos. 1 and 2, but letʼs consider the addition of new Exception No. 3.
Exception No. 1 will permit up to 6 feet of unprotected (AFCI) branch-circuit conductors where installed in a metal raceway or a metal-sheathed cable. This was done more as a convenience to establish a level playing field for the use of receptacle type AFCIs than for safety reasons.
Exception No. 2 will permit an unprotected (AFCI) ?individual branch circuit? supplying a dedicated (marked) outlet for life-support equipment in
dwelling unit bedrooms. An ?individual branch circuit? can serve only one utilization equipment and at least three circuits (PCA pumps, Feeding pumps, Respirators, Beds, etc.) may be needed. This means, that for three such circuits at least 90 feet, on an average, [up the wall (8 ft.), across the ceiling (15 ft.), and down the wall (7 ft.)] (3 x 30 ft. = 90 ft.) may be needed. Consider the use of 90 ft. of unprotected (AFCI) cable (any cable method, not metal raceway or metal-sheathed cable). But, then consider not permitting 3ʼ of cable (of any type) located over the bedroom entry door to supply a life-saving smoke detector. The location above the entry door is virtually free from any physical injury and it is unrealistic to think that a nail, etc. would be driven in that location.
If an AFCI device operates on a bedroom outlet (receptacle or lighting), the worst scenario is to reset the clock radio. A smoke detector is not a bedroom outlet per se, it is a smoke detector outlet located in the bedroom to rouse sleeping families in fire or smoke situations. Smoke detectors are a life-saving device and it is unthinkable to compromise this circuit by connecting it to a sensitive AFCI protected circuit.
Panel Meeting Action: Reject
Panel Statement: The submitter has not provided Panel 2 with any documentation to support his claim that AFCI devices are not compatible with listed smoke or burglar alarms.
Number Eligible to Vote: 13
Ballot Results: Affirmative: 10 Negative: 3
Explanation of Negative:
BECKER: See my explanation of negative vote on comment 2-70.
DOBSON: With AFCI technology still in its infancy it is clear there are many uncertainties. The CMP has decided to redefine the technology because
it does not supposedly provide all of the desired protections. The CMP has decided to hold off on any expansion of the device in new construction until
enough field data has been provided. We do not know everything about AFCI technology and how it will perform. There is enough skeptisism to warrant not taking a chance on having the AFCI technology impede the performance of a proven technology that has been around for well over 30 years. We should not compromise the single most important fire safety device in one-and-two family dwellings - smoke alarms. This requirement not only impacts the smoke alarms in the bedrooms but also will effect the entire smoke alarm system, as interconnected smoke detectors are required by manufacturers to be wired on the same circuit.
OʼNEIL: The panel has rejected this comment because the submitter has not provided substantiation that AFCIs are not compatible with listed alarms.
Manufactures have submitted that current product standards does permit nuisance tripping on products listed to UL 1699-1999. Until any question of the possibility of nuisance tripping is resolved, AFCI devices should not be permitted on life saving devices. Putting AFCI protection on Life Safety devices creates the greater risk of disabling life saving devices at the time proper operation of the life-safety device is most required.
[ April 05, 2004, 12:25 PM: Message edited by: don_resqcapt19 ]