Re: 4/0 cable into the back of a 3 1/2 inch deep panel
Hi Guys,
Table 312.6(A) is the correct table to use in this installation.
This is from the Handbook;
Hi Guys,
Table 312.6(A) is the correct table to use in this installation.
This is from the Handbook;
Section 312.6(B)(2) and Table 312.6(B) provide the requirements for wire-bending space where straight-in wiring or offset (double bends) is employed at terminals. Section 312.6(B)(1) applies only to 90 degree bends.
Note that in accordance with the notes to Tables 312.6(A) and 312.6(B), when using Table 312.6(A), bending space is measured in the direction in which the wire leaves the terminal, and when using Table 312.6(B), it is measured in a direction perpendicular to the enclosure wall.