You must use a breaker rated 23.44 amps or above.4500w heater 240V 18.75A *1.25= 23.44
422.13 Storage-Type Water Heaters.
A branch circuit supplying a fixed storage-type water heater that has a capacity of 450 L (120 gal) or less shall have a rating not less than 125 percent of the nameplate rating of the water heater.
210.3 Rating.
Branch circuits recognized by this article shall be rated in accordance with the maximum permitted ampere rating or setting of the overcurrent device. The rating for other than individual branch circuits shall be 15, 20, 30, 40, and 50 amperes. Where conductors of higher ampacity are used for any reason, the ampere rating or setting of the specified overcurrent device shall determine the circuit rating.
I still am not following you.Branch Circuit. The circuit conductors between the final overcurrent device protecting the circuit and the outlet(s).
This requires that the branch circuit (not just the conductors...the BRANCH CIRCUIT) be sized at 125%. The rating of a branch circuit is determined by the size of the overcurrent device, not the conductors.422.13 Storage-Type Water Heaters.
A branch circuit supplying a fixed storage-type water heater that has a capacity of 450 L (120 gal) or less shall have a rating not less than 125 percent of the nameplate rating of the water heater.
You are correct the breaker is not part of a branch circuit, but as directed by 210.3 the breaker rating determines the rating of the branch circuit connected to it.Originally posted by howlev:
THE CIRCUIT CONDUCTORS FROM THE LUGS OF THE OVERCURRENT DEVICE TO THE OUTLET BRANCH CIRCUIT DOES NOT INCLUDE THE OVERCURRENT DEVICE OR THE OUTLET IN THIS CASE THE WATER HEATER
yOU
Section 2102 does not say "AN APPLIANCE BRANCH CIRCUIT IS NOT RECOGNIZED IN THIS ART." Section 210.2 says that other articles may amend or supplement the provisions of 210.Originally posted by howlev:
MAY ALSO WANT TO LOOK AT ART 210.2 AS AN APPLIANCE BRANCH CIRCUIT IS NOT RECOGNIZED IN THIS ART. AS STATED IN ART.210.3 BUT IS RECOGNIZED IN 422