Voltage drops to zero from 110 under load

Status
Not open for further replies.

FastTracker

Member
Location
Pittsburgh Pa USA
Occupation
Wireman, Superintendent, Estimator
an old mercury vapor has 110 at the socket until you put a load on it then it goes to zero? I am thinking a loose neutral at the source or a broken/loose wire in the run somewhere with an induced voltage any ideas?
 

iwire

Moderator
Staff member
Location
Massachusetts
an old mercury vapor has 110 at the socket until you put a load on it then it goes to zero? I am thinking a loose neutral at the source or a broken/loose wire in the run somewhere with an induced voltage any ideas?

You are on the load side of the ballast, have you checked the voltage on the supply side of the ballast.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I also agree - bad connection. The connection is enough to read voltage but when a load is applied there isn't enough of a connection to carry the load.
 