Ufer Grounding

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
Re: Ufer Grounding

I believe I saw it posted that at least one area requires the rebar to stick out of the footing to make the GEC connection visible.

NJ? FL?
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: Ufer Grounding

Pierre, I am referring too where you would stub up a single piece of rebar for connecting the GEC. I do this inside the electrical room, not outside.

Where I bond the rebar to a ground ring, I specify copper cable in the footing to exit at strategic locations around the perimeter.

[ February 23, 2004, 05:49 PM: Message edited by: dereckbc ]
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Ufer Grounding

Dereck,
I am referring too where you would stub up a single piece of rebar for connecting the GEC. I do this inside the electrical room, not outside
this is a common installation in my area also. We will either be on the job at this time or go by and attach a piece of rebar before the pour.

We usually stub this up inside the Main Switchboard.

Roger
 
A

a.wayne3@verizon.net

Guest
Re: Ufer Grounding

In this area a slab can`t be poured without a ufer inspection,some areas differ.some want rebar stubbed out just below grade level,some require #4 connected to the rebar in the footer.But regardless of which no concrete is poured without uffer signed off.
 
A

a.wayne3@verizon.net

Guest
Re: Ufer Grounding

Roger to do that you would have to have a basement non here......Unless you stubbed it out of the slab
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Ufer Grounding

Allen, as I said, we attach a piece of rebar (to the footer steel) and run it to the location.

As a matter of fact, I've done the same thing in your part of the world.

Roger
 