Can someone point me in the directions in which I can find illustrations on ufer grounds. I know what they are, and what they do, but I've never seen the actually lay-in process. I need more visuals.
Yes that is true, but what we electricians typically call a Ufer is only a concrete encased electrode.Originally posted by dnbob:
The term "UFER" is not exactly a generic term, it was named after the guy that invented it,
Hi Derek,Originally posted by dereckbc:
Patty, the Ufer ground can be as minimal as required by the NEC or as elaborate as what military, telecom and broadcast performs.
I would caution anyone using the minimum requirements of # 4 AWG laid in the bottom of the footing. I learned the hardway. In the rare event the site should be struck by lightning, you could suffer foundation damage.
In the telecom industry we require all the re-bar to be bonded together either by double tie wires, irreversible compression, or exothermic weld. I stub up a rebar near the AC service entrance and where ever I need access to the GE system, then weld the GEC or bonding jumper to the rebar. Its that simple, and fairly economical.