Re: two-wire travellers and emf
This thread is such a thorough discussion of 3-way wiring that I am reluctant to leave it before finishing the discussion.
Hbiss posted that 300-3(b) says that the grounded conductor must be run with the other conductors "where used". And he prefers not to use it. All 120V circuits use a grounded conductor. 240V may not. The question with the 3-way circuit is where you run the neutral, not whether you run it.
Do you run it with the hot or do you run it separately through the wall between switches or the receptacles feeding the switches?
Before the 1999 NEC NM was not excepted from 300.3(b). Why it was excepted in '99 I would be interested to know, as it seems to be a step backward. However, if you use this exception and run your neutral away from the hots (travelers) you also have to comply with 300.20(B). This requires you to cut a slot in any ferrous metal between the separated conductor and it's accompanying conductor/s, to reduce the heat buildup.
So if your traveler hot enters any ferrous junction box or fluorescent fixture without it's neutral you have to start cutting. But how do you do this if the neutral is 10 feet away in the wall. Any ferrous box the neutral goes into will also need a slot between it and the hot, so you have the same situation. The heat buildup that 300.3(B) is trying to avoid will occur, since the other conductor is far away. So how can this be Code compliant? Obviously they were not considering the possibility that one conductor would be run in an entirely separate path.
It was mentioned in this thread that if hot and neutral are derived from a single circuit maybe 2-conductor travelers are OK. But this means you have a circuit running through the wall with only one conductor carrying current, either the hot or the neutral. The traveler carries one current-carrying conductor and the circuit in the wall between the switches carries the other current-carrying conductor.
This sets up a large loop. The magnetic field inside a loop is large and very uniform, so the calculation of the magnetic field I mentioned in my preceding post has to be modified, since the field does not continue to weaken, but builds up again as it approaches the other side of the loop.
About liability, mentioned as a red flag by hbiss: no electrician is going to be sued for following the NEC. There may be liability issues in the future based on having knowledge of possible or probable health effects and then failing to use this knowledge in electrical installations, just as in the cigarette industry, but the electrician is protected by following Code. Many electricians create high fields by not following Code. Someday there will be a landmark lawsuit.
Meanwhile, Code allows you to use 3-conductor travelers in 3-way switching; the wiring manuals show it as the correct way, so why not do it?
That's it for me! As they say, thank you for your attention....
Karl