At the commercial job I'm presently on, there are three-way switches at opposite ends of a U-shaped corridor which operate eight or so 2x4 120v fluorescent fixtures. A two-wire MC (100') was run from switch to switch for travellers, which I realize should rather have been a three-wire, and wish I had caught the mistake before the ceiling insulation, grid, tile, etc., went in, because now it'll be an ugly job to replace.
In 300.20 it says all phase conductors and, where used, the grounded conductor and EGC shall be grouped together, but I'm unable to find the reference for travellers needing a neutral to counter EMF.
Do travellers in-fact absolutely need a 3-wire? What levels of EMF would be expected in a case like this? How much EMF is involved in loaded switch loops, and why aren't switch loops required to include neutrals if travellers are?
Thanks for any responses.
In 300.20 it says all phase conductors and, where used, the grounded conductor and EGC shall be grouped together, but I'm unable to find the reference for travellers needing a neutral to counter EMF.
Do travellers in-fact absolutely need a 3-wire? What levels of EMF would be expected in a case like this? How much EMF is involved in loaded switch loops, and why aren't switch loops required to include neutrals if travellers are?
Thanks for any responses.