I sent this off to the NFPA but would appreciate any input:
I work for a regulatory agency that has adopted the NEC and NFPA 99 and have the following technical questions in reference to NFPA 70 -2002: 517.30 and NFPA 99 - 2002: 4.4.2.2
1. For a Type 1 EES in a hospital, is it permissible to connect a smoke damper to the Emergency System-Critical Branch? ( The smoke damper protects a duct penetration in a smoke barrier wall and the damper is not part of an engineered smoke control system.)
2. Is the damper considered an auxiliary part of the fire alarm system and required to be connected to the Emergency System - Life Safety Branch?
3. Although not part of a engineered smoke control system, can the damper be connected to the Equipment System since it does serve to control smoke passage at the smoke barrier wall?
I work for a regulatory agency that has adopted the NEC and NFPA 99 and have the following technical questions in reference to NFPA 70 -2002: 517.30 and NFPA 99 - 2002: 4.4.2.2
1. For a Type 1 EES in a hospital, is it permissible to connect a smoke damper to the Emergency System-Critical Branch? ( The smoke damper protects a duct penetration in a smoke barrier wall and the damper is not part of an engineered smoke control system.)
2. Is the damper considered an auxiliary part of the fire alarm system and required to be connected to the Emergency System - Life Safety Branch?
3. Although not part of a engineered smoke control system, can the damper be connected to the Equipment System since it does serve to control smoke passage at the smoke barrier wall?