Re: Service Neutral
Bennie you always seem to look at this like the generators always pick up entire buildings, I have never seen that, always generators that pick up bits and pieces of buildings.
The generators we install do not pick up the entire building.
We have many buildings that have multiple generators, one will be for the Article 700 loads, the others and they may be quite a few are owned by individual tenants for there use to keep them in business.
Dumping a GFP on a dead feeder is very difficult.
Once a week the generators run for exercise about 30 to 60 minutes, multiply that by the number of generators that the building has and you find a lot of time when both systems are active and could dump the GFP mains.
Parallel current has nothing to do with the reason for switching the neutral.
Bennie what the heck do you mean?
You do not see the parallel path for neutral current on the GEC in Eds drawing?
Or you feel that this circulating current that could be 100s of amps is OK?
This seems to fly in the face of your opposition to the low levels of current flowing between grounding electrodes in the earth.
The purpose of transferring the neutral is to prevent the generator from feeding into the utility line. And the utility neutral from feeding into the generator line..........................
Now everyone is going to say "how can one feed into the other" Think of a LN fault, the neutral will be energized until the fault clears.
Call me one of the everyone, I do not understand this, how would the generator feed into the utility line.
Please explain with more than one sentence, where is the "other" conductor for this circuit to feed or return current on?
A line to case fault would only circulate current between the generator and the bonding point, well away from the utility workers.