Hello everyone!
This is indeed a very good thread! A major thought processing one - covering the NEC in several Chapters, along with a bit of Designing Issues.
** O.T.: Just saw the Movie "Ray" (about Ray Charles Robinson, known simply as "Ray Charles"), and it was excellent!
Anyone interested in Music would enjoy this film.
OK, so much for the Movie Plug
< soapbox mode = ON >
The questions brought forth by Roger are quite interesting and debatable, but sometime soon Concrete answers will be derived. Might not be what everyone wanted to see, but nevertheless they will be what is per NEC minimums.
< soapbox mode = OFF >
I am looking at this scenario in several ways, and would like to offer my opinions only.
First off, I would like to toss out the normal recommendation of not using the term "Subpanel", in place of the term "Panelboard".
Reason being is this situation may not qualify for what we would figure as a "Subpanel".
(BTW, I am trying to eliminate the terms "Subpanel" and "Subfeeder" from use at work - and it isn't easy!).
#1: The "Grounding Thing":
In my opinion, what is done for separation of EGCs from the Grounded Conductors' Bus (at the remote Panelboard), would be in the idea set forth in 250-32 (99 NEC), or 250-24 (prior to 99 NEC).
Is there any Conductive path for imbalanced Current to flow between the remote Panelboard and the Service Equipment?
Bennie brought this one up quite a lot.
Even though it will be a Remote Panelboard, must we "Re-Ground" the Grounded Neutral Conductor at this Panel (connect it to an Electrode at that Panel), simply because the Neutral Bus Kit is directly Bonded to the Enclosure?
At Remote Structures we may do as described, but we also bond the Grounded Neutral Conductor to a Local GES.
We may also include an EGC with the Feeders to a Remote Structure's Panelboard, and in this case the Grounded Conductors for the Branch Circuits would land upon a Bus, which is _Isolated_ from the Grounded Enclosure. We will also bond the Metallic Equipment / Enclosures, along with the EGCs, to a Local GES at the Remote Structure.
To me, the Grounded/Grounding Conductors, on the Panelboard in question per this thread, would fall in lines of "If They May Be Allowed To Land Together, AND Also Bond The Panel's Enclosure", more than anything else.
If someone can produce facts of why this may, or may not be allowed (per what the NEC Articles/Sections state), please do so!
Although I do not install Remote Panelboards in this fashion (Ground Bonding, that is), it does not necessarily mean anything is incorrect.
#2: Extension of Service Equipment or Aux. Panelboard..Just what is it now?:
Well, at first I was thinking like Pierre's post mentioned; the Proximity of the Secondary Panel.
I see Panels being fed via "Feed-Thru Lugging" as an extension of the first Panel's Bus, but also right next to the first, or "Supplying" Panel.
"Next to" as being within the same room, normally nippled together, but not necessarily always that close - at least the two Panels are within the same room.
That again is only my opinion, brought on from what is "Commonly Seen/Done In The Field" over the Years.
To me - and again, just my opinion - any Panelboards (Load Centers, Panelboards, Switchgear, MCC) not _Physically_ connected to the Service Equipment (Service Equipment containing the Service Disconnecting means, along with the first point of connection for the Grounded Conductor to the GES - and possibly having the KWH Meter included, but not necessary), are Auxillary or Remote Equipment - and therefore do not qualify as being part of the Service Equipment.
The "Catch" on this thinking, comes from the use of an ATS!
To wrap things up, I would call the Panel a Remote Panelboard (or a "Subpanel"), simply because it is not in the same location of, or physically connected to, the Service Equipment.
(When I say "Physically Connected", I mean bolted or fastened together, or nippled together no further than a few feet apart).
As to the Grounding/Grounded Conductors and methods, I could see either method being valid.
Would love to know if my opinions are anywhere close to correct!
Scott