Paintbooth Enclosure Wiring

faresos

Senior Member
The specified fixture is not rated for any hazardous location since we are complying with 516.6C(1) but I was asking about figure 516.5(D)(4) if inside the wall included as part of the hazardous area or not because the way I see the figure it's not included but you are saying this illustration maybe miss presented it and should be included. This will be a major change as it happens in several locations and I was hoping to find some exception that can allow this installation but it appears there is none. Thanks for your time
 