jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
Say service conductors come out of the slab directly into a gutter that branches to up to six disconnects directly above the gutter. Allowed? I would think so.I agree with Don's interpretation that the "taps" inside the building ahead of the normal main breaker will be subject the AHJ allowance , if at all. Any supply-side connection to the service entrance conductors in that panel ahead of the main that "extends" those service entrance conductors, would be beyond what is already been permitted with the existing installation.
...
Now what is the meaningful difference between that and a supply-side tap inside existing service equipment to a disconnect immediately adjacent? I would say there is none.
Just my opinion that both should be allowed. I suppose a given AHJ could allow or disallow either one, but I'd expect them to be consistent.