pkhosravani
Member
- Location
- Austin, TX
- Occupation
- Solar
Comparing NEC 2020: 705.11 to NEC 2023: 705.11, there looks to be some important changes - possibly helpful changes - for the PV industry. With that said, I'm not an expert and because NEC 2023 was just released, I've been unsuccessful in finding clarification thus far, so I'm putting it to the members of this forum to help a novice, like myself, understand the changes and their implications for interconnecting PV to the supply side.
In particular, NEC 2020: 705.11 (c) (1) through (c) (2) are totally gone, missing, disappeared from the NEC 2023 code.
The NEC 2020: 705.11 (c) (1) required an overcurrent device be located within 3m (10 ft) of conductor length in dwelling units and 5m (16.5 ft) in other than dwelling units from the point of connection to the service. Followed by section (c) (2) that allows for current limiters on all ungrounded conductors if the overcurrent device is located within 20m (71 ft) of conductor length from the point of connection to the service, etc, etc.
With both (1) and (2) gone from the code, it looks to me that we when making a supply-side connection of electric power production sources (aka PV) we can now have an infinite length of conductor between the our supply-side connection point (usually an IPC or a insulated multi-tap connector commonly referred to as a Polaris block) to the nearest OCPD, which is usually the PV-Utility AC disconnect switch located outdoor & fused. Is that correct? Did I miss anything? Am I way off base?
In particular, NEC 2020: 705.11 (c) (1) through (c) (2) are totally gone, missing, disappeared from the NEC 2023 code.
The NEC 2020: 705.11 (c) (1) required an overcurrent device be located within 3m (10 ft) of conductor length in dwelling units and 5m (16.5 ft) in other than dwelling units from the point of connection to the service. Followed by section (c) (2) that allows for current limiters on all ungrounded conductors if the overcurrent device is located within 20m (71 ft) of conductor length from the point of connection to the service, etc, etc.
With both (1) and (2) gone from the code, it looks to me that we when making a supply-side connection of electric power production sources (aka PV) we can now have an infinite length of conductor between the our supply-side connection point (usually an IPC or a insulated multi-tap connector commonly referred to as a Polaris block) to the nearest OCPD, which is usually the PV-Utility AC disconnect switch located outdoor & fused. Is that correct? Did I miss anything? Am I way off base?