I have chagrining station site fed from 50A breaker 208V single phase. Due to voltage drop designer uses #6 phase conductors. However he is not sure if temperature termination if its 75C or 60C.
So in order to upsize the equipment grounding conductor if designer uses #6 then it comes to #4. However if terminal ratings are 75 then he has to use #8 in which case equipment grounding conductor would be #3.
Designer says he can use 60C Even though he does NOT know the temperature rating of terminal/equipment based on NEC 2014 section 110.15(C)(1)(a) and he does not need to upsize equipment grounding conductor.
Is the designer right or wrong?