See existing #8 service drop on panel flipper's outdoor 100A breaker HOM20M100RB
This #8 wire is type TW, 40A max, since not listed beyond 60° C.
NEC 230.79(C) says 100A disconnect is OK
2pole 40A breaker in building #1 protects customer-side drop for this panel at building #2.
Is existing 40A Service drop allowed here?
This #8 wire is type TW, 40A max, since not listed beyond 60° C.
NEC 230.79(C) says 100A disconnect is OK
2pole 40A breaker in building #1 protects customer-side drop for this panel at building #2.
Is existing 40A Service drop allowed here?