That is coming right off the meter yesIf that is straight of the load side of the meter your set up looks like it is not rated as ”service equipment “
I have a set of SECS not a feeder that's the whole argument I believeI don't see a tap there. You have a feeder going to a breaker panel with two breakers.
That strap and green screw below the lower breaker, is that a factory neutral-ground bond? So the panel is marked "Suitable for Use as Service Equipment?"I have a set of SECS not a feeder that's the whole argument I believe
At least he's using Mike Holt as a source of learning. That shows good characterHe definitely did, it's a serious problem here in NYC very under qualified inspectors.
The breakers are not in parallel, unless their load sides are connected together.There's something weird about that drawing. They call the top breaker the main, but both breakers are in parallel.