Back feeding a panel is often done but a retainer clip must be installed to insure the breaker is fastened. Look at art.408.36(D)
I don't do solar but I believe you may not need to use the retainer clip
Solar applications specifically do not require a retaining method for the backfed breaker, when you connect the inverter side to the branch terminals.
The reason for requiring a retaining clip is that, in the event that the plug-on breaker is unplugged from the busbar, you want to avoid energizing the breaker. If an inverter breaker is unplugged from the busbar, the circuit is still deenergized, even if the inverter was recently operational.
An interesting case not explicitly covered by the code, is what happens when you use a plug-on branch breaker as the main breaker of a panelboard that is backfed? I recently built a load center to combine two 40A inverters into an 80A output, with an 80A branch breaker used as a main. The circuit is still energized, even if you unplug the 80A plug-on breaker. Therefore, it is my opinion, that even though this breaker is
forward fed per the power flow direction, it is still
reverse energized by grid voltage on the branch terminals. And thus it should have a retaining clip.
Another check you always have to do, is whether the breaker is built to be backfed. If it is not marked "line and load", then it is suitable for backfeed. This can be a difficult thing to look up, because you are trying to prove a negative. You look at the only part of the breaker you can see, in the existing main panel, and you prove that it isn't already marked line and load.
The typical off-the-shelf ordinary breaker usually is suitable for backfeed. It is usually breakers with additional functionality, such as AFCI and GFCI that might not be. Microinverter users are in a Catch-22. They need to tie-in at an AFCI breaker, but no backfeedable AFCI breakers exist yet.