As a side note, I have worked with customers that installed a fused disconnect after the meter Ahead of the original main panel to de-rate the fault current.
Too bad this is not a very good solution.
I have seen it do no good in more situations than it has helped.
Fuses do not actually reduce fault current until they melt and clear. So for medium and low level faults, large fuses may be no better than bus bars.
There is a reason the NEC requires protective devices to be tested in series, or to be engineered by a licensed professional (but only for existing installations).