This discussion came up during a chat session last night on the ECN Forum. I thought I should post this issue to get this Forums opinion.
The NEC requires the small appliance, laundry, and bathroom circuits to be 20A rated citcuits. The code also allows 15A rated devices on 20A branch circuits as long as the load on any one receptacle does not exceed 80%. Here's the question.
Many appliances, like the example of a 1875-Watt hairdryer, have loads that exceed the 12A allowance of a 15A receptacle that will commonly be found on the 20A bathroom receptacles. NFPA and NEMA sleep in the same bed and must be aware of this issue. The cords on the appliance are only 15A rated cords but the are being used on 12A limited devices.
So, it is my opinion that once a 15A device is installed on a 20A rated circuit, you have effectively reduced that citrcuits capacity to a 15A rated circuit and you would then be in violation of the 210.11(C) requirements.
I know in many cases, the installer has no control of what loads and how much load will be used by the user. But in this case, the problem could easily be avoided by simply requiring and installing 20A rated receptacles on 20A rated circuits. This way, a greater than 12A rated load would not be a problem and the entire 16A allowance of a 20A rated circuit could be used.
Any thoughts?
The NEC requires the small appliance, laundry, and bathroom circuits to be 20A rated citcuits. The code also allows 15A rated devices on 20A branch circuits as long as the load on any one receptacle does not exceed 80%. Here's the question.
Many appliances, like the example of a 1875-Watt hairdryer, have loads that exceed the 12A allowance of a 15A receptacle that will commonly be found on the 20A bathroom receptacles. NFPA and NEMA sleep in the same bed and must be aware of this issue. The cords on the appliance are only 15A rated cords but the are being used on 12A limited devices.
So, it is my opinion that once a 15A device is installed on a 20A rated circuit, you have effectively reduced that citrcuits capacity to a 15A rated circuit and you would then be in violation of the 210.11(C) requirements.
I know in many cases, the installer has no control of what loads and how much load will be used by the user. But in this case, the problem could easily be avoided by simply requiring and installing 20A rated receptacles on 20A rated circuits. This way, a greater than 12A rated load would not be a problem and the entire 16A allowance of a 20A rated circuit could be used.
Any thoughts?