So I'm in Vermont and a friend of mine is building a barn and I noticed that his service has xhhw-2 wire run on the outside of the wall. I've never seen that before. We would not do this in Colorado. Is this normal around the country?
 

Attachments

  • Screenshot_20221019_183638.jpg
    Screenshot_20221019_183638.jpg
    411.8 KB · Views: 66

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
So I'm in Vermont and a friend of mine is building a barn and I noticed that his service has xhhw-2 wire run on the outside of the wall. I've never seen that before. We would not do this in Colorado. Is this normal around the country?
Pretty typical around my parts. Although it’s an eye sore and in some scenarios is “subject to physical damage”.
 

Rick 0920

Senior Member
Location
Jacksonville, FL
Occupation
Electrical Instructor
You guys run uf exposed on outside of building? Never see se cable exposed like that. Only seen if once!
Here in Florida a lot of homes built in the 50's and 60's had SE cable strapped to the block and used an SE weatherhead. It's not common today, but most AHJ's will still allow you to use it for repairs.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Here in Florida a lot of homes built in the 50's and 60's had SE cable strapped to the block and used an SE weatherhead. It's not common today, but most AHJ's will still allow you to use it for repairs.
What right does the authority having jurisdiction have to turn it down. It is compliant. Personally I would never use it but it's done alot in the NE. I remember Bob Badger saying he ripped out a job(maybe his own home) that had pvc and he install se cable as the riser. To each his own
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I don't see a problem with it run exposed and as mentioned it can look better than a raceway because it's less conspicuous. We run it into and out of the meter pan when there is no likelihood of physical damage. If the meter is over a driveway or sidewalk where it could get hit by a snow blower or vehicle then we would use a raceway for protection but for something like a flower bed the SE runs right into the house.
 
What right does the authority having jurisdiction have to turn it down. It is compliant. Personally I would never use it but it's done alot in the NE. I remember Bob Badger saying he ripped out a job(maybe his own home) that had pvc and he install se cable as the riser. To each his own
Yup. I would probably do the same thing, rip down the PVC and put up SE cable, I hate PVC above ground
 

Rick 0920

Senior Member
Location
Jacksonville, FL
Occupation
Electrical Instructor
What right does the authority having jurisdiction have to turn it down. It is compliant. Personally I would never use it but it's done alot in the NE. I remember Bob Badger saying he ripped out a job(maybe his own home) that had pvc and he install se cable as the riser. To each his own
The right they have I guess is that they have the authority to supersede the NEC if they are more stringent. In Orlando, for example, your (2) small appliance circuits can't have more than (2) duplex receptacles on them. (That's how it was when I left there in '98) In 2008, Oklahoma City's Building Dept. requires you to use the colors black, red, blue for respective phases on 120/208 systems. So we had to start buying MC that was red, white and green and blue, white and green.
 

AC\DC

Senior Member
Location
Florence,Oregon,Lane
Occupation
EC
That’s
The right they have I guess is that they have the authority to supersede the NEC if they are more stringent. In Orlando, for example, your (2) small appliance circuits can't have more than (2) duplex receptacles on them. (That's how it was when I left there in '98) In 2008, Oklahoma City's Building Dept. requires you to use the colors black, red, blue for respective phases on 120/208 systems. So we had to start buying MC that was red, white and green and blue, white and green.
unless it’s in your state electrical amendment they cant
go beyond the code.
When it a vague rule then they have some power other than that they much follow state and nec
 