That just means that instead of truly infinite current in an "idealized" short circuit, you get the available fault current feeding a real world fault instead. Available fault current, usually measured in kiloamps, which is a function of the voltage and impedance of the source and distribution system. The heat generation ends up being inside the source and wires to an extent they aren't meant to be heated, rather than as usable power delivered to the load where we intend to use the power.So instead of using reality, you're proffering theory. I mentioned this already. I work in the real world, not a theoretical one.
An intended load with “very low resistance” is not a short.So a short circuit is just a resistive load with a very low resistance.
With respect, I don't agree with that. You can have a fault between live and neutral. That isn't a the same as ground fault.I had been taught that as well, simple yes but that definition would also include a ground fault which IMO is not the same as a short circuit. I think of a short circuit as a shortcut between normal current carrying conductors.
So I guess we call both a ground fault and a short circuit a short?
A fault between any two live conductors, or the live conductor and the neutral, would be what the NEC would term a short circuit. A fault between any two conductors that are built for carrying current under normal non-fault circumstances, even if no loads are set up to put current on the neutral.With respect, I don't agree with that. You can have a fault between live and neutral. That isn't a the same as ground fault.
Thank you, sir. Pretty as I see it also.A fault between any two live conductors, or the live conductor and the neutral, would be what the NEC would term a short circuit. A fault between any two conductors that are built for carrying current under normal non-fault circumstances, even if no loads are set up to put current on the neutral.
A ground fault works just like a short circuit, the way the term is defined in Physics, but with the added hazard of normally non-energized metal, becoming electrically energized. There also may be more resistance in a ground-fault current path, than in the return-path between current-carrying conductors, so the ground fault current could be a lot less than the short circuit fault current on the same circuit. The NEC doesn't include a ground fault in its vocabulary of a short circuit, because a ground fault is a separate safety issue with its own requirements for mitigating.
But shorting jumpers can be added when you want to work on things safely (e.g. CTs). I'd say a fault is an untended pathway. It could have high or low resistance.An intended load with “very low resistance” is not a short.
A short is an unintended path causing current to bypass the intended load.
If it has a high resistance, it is not a "short". Similarly, if it has a high impedance in other forms (e.g. inductance), it is also not a short.But shorting jumpers can be added when you want to work on things safely (e.g. CTs). I'd say a fault is an untended pathway. It could have high or low resistance.
The CT is the source. The load is the attached measuring device. So by shorting a CT, you are bypassing the intended load.But shorting jumpers can be added when you want to work on things safely (e.g. CTs). I'd say a fault is an untended pathway. It could have high or low resistance.
In a typical DC motor, the armature is a bar and a short between the brushes. That high current flow gives DC motors typical high torque at starting, limited by the resistance through the brushes and the supply system inpedance.On a similar thought, why doesn't a motor short through its brushes(I admittedly have a narrow understanding of motors)?
thanks
Well if you had a perfect conductor with absolutely zero resistance, and jumped it across a voltage source current is still limited by the impedance of the source.We can talk about 'there is no such thing as infinite resistance' and 'there is no such thing as a perfect conductor'. Yes, technically all insulation is in reality a semi-conductor. But that's theory, not in actual practice.
Then throw in an ungrounded system, a ground fault there generally doesn't cause any significant abnormal current, it just turns makes an unintended ground reference. A second ground fault is where you get unintended current on this system.A fault between any two live conductors, or the live conductor and the neutral, would be what the NEC would term a short circuit. A fault between any two conductors that are built for carrying current under normal non-fault circumstances, even if no loads are set up to put current on the neutral.
A ground fault works just like a short circuit, the way the term is defined in Physics, but with the added hazard of normally non-energized metal, becoming electrically energized. There also may be more resistance in a ground-fault current path, than in the return-path between current-carrying conductors, so the ground fault current could be a lot less than the short circuit fault current on the same circuit. The NEC doesn't include a ground fault in its vocabulary of a short circuit, because a ground fault is a separate safety issue with its own requirements for mitigating.
In your real world, if a circuit has NO resistance, does current flow?So instead of using reality, you're proffering theory. I mentioned this already. I work in the real world, not a theoretical one.
Hmm, in my REAL world No resistance is zero (0) Ohms, and can flow lots of current.If a load doesn't have some resistance, current cannot flow.
Though it may be impossible to achieve resistance of zero, isn't that the concept behind "superconductors" is to achieve as little resistance possible to increase current carrying ability?In your real world, if a circuit has NO resistance, does current flow?
Hmm, in my REAL world No resistance is zero (0) Ohms, and can flow lots of current.
Hence your statement is wrong, as if there is no resistance, lots of current will flow. That's why posters are pointing out the flaw.
Infinite resistance (Insulator) is quite a LOT of resistance! Not Zero. And no current flow.
Also if there is NO resistance, you get a divide by zero error.... in I = E/R so use .00000000001 ohms instead.
On the other topic, when people say "it has a short" when describing a lamp that flickers as the cord/switch is moved, I correct them and say "Nope, it has a long" and they don't understand....![]()
And that's how we calculate short circuit current available.If you have zero resistance or even super low resistance, and no load in the circuit to add resistance to the circuit then the only thing limiting current in that circuit is the impedance of the source.