Look around the pump motor or timer, or any other equipment for the pool. You probably won't see it in the panel as its not required to be there.
 

spark master

Senior Member
Location
cyberspace
ok,, it's running up the back of a 4x4 post which supports the pool panel.... and goes directly into the pool panel.
The aged copper actually blends in pretty nicely with the pressure treated post, which is covered in vegetation.
But anyway, goes directly into the pool panel, and I don't see split bolts or anything to make taps for the pump ground & heater ground....
 

augie47

Moderator
Staff member
Location
Tennessee
That one is likely not part of the pool bond grid (more likely a panel grounding electrode).
As suggested above. Look at the pump.
 