I am trying to find out what is different about the different types of wire. Example the difference between size 14 AWG Type TW and size 14 Type THHN. Where can I get this type of information?
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: what do the wire types mean

Table 310.13 Conductor Application and Insulations

TW for example is Flame- retardant, moisture -resistant thermoplastic. For dry or wet locations, with a maximum operating temp of 60 C

THHN is Flame- retardant, heat-resistant thermoplastic for dry or damp locations with a maximum operating temp of 90 C
 

Nick

Senior Member
Re: what do the wire types mean

There is a pretty significant difference in size between TW and THHN as well. TW is pretty tough to pull and almost never seen anymore in new installations.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: what do the wire types mean

The letters describe the type and rating of the insulation. The ?T? stands for ?thermoplastic.? It is good for a 60 degree C temperature rise, with an ambient temperature of 30C. The ?H? stands for ?add one measure of heat.? It means that you add 15 degrees C to the temperature rating. So a ?T? is good for 60C, a ?TH? is good for 75C, and a ?THH? is good for 90C. The ?W? stands for ?wet,? and tells you the conductor can withstand a wet environment.

The ?AWG? stands for ?American Wire Gauge.? The bigger the number, the smaller the wire. For example, most household circuits will use a #12. A #14 is smaller than this, and a #10 is bigger. The size of the wire is related to the amount of current it can safely carry. The larger the wire, the more current.
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: what do the wire types mean

To add to what Charlie said, R is for thermoset rubber, and -2 is another heat measure. For example a cable listed RHW-2 is ruber insulated, 90 degree, wet or dry locations.

X is another designation for for cross-linked thermoset plastic for example XHHW-2 would be Cross-Linked synthetic polymer rated for 90 degrees is wet locations.

It is a little confusing at times. But genneraly the first letter or two designate the insulation type followed by heat a water designation, but not always. For example FEP and FEPB is Fluorinated Ethylene Propylene (Teflon) 90 and 200 degree respectively, dry and damp locations.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: what do the wire types mean

Oops! Yes, it is nylon. Should not have gone from memory, for tis the memory that is gone.
 