Re: Well casing as Grounding Electrode
Scott, the key in my mind is: Is the well present at the structure, or is it 30' away from the structure?
In general, IMO, 250.122(M) (off the top of my head, that might not be quite right) leads me to believe that while you could use the well casing as an electrode if you were to run clear out to it, the NEC considers the copper pipe entering the structure from the well to be the electrode. The casing would need to be bonded to the BC EGC.
If you were to try to use it as an electrode, I'd say it is part of 250.52(A)(1). The parenthetic "(including any metal well casing effectively bonded to the pipe)" states that, while the CMP recognizes that the primary function of the well casing is not acting as a "water pipe", they intentionally ignore that fact. When bonded to the pipe carrying the water, the metal well casing is by NEC standards part of that water pipe.
With that, your metal well casing would require a supplemental electrode per 250.54. or .56, whichever it is.
Too lazy to open the book this morning.