I had a friend of mine call today he's a plumber.

He was using a metal snake and the snake hit the ground rod for the panel and he kept getting blasted

I'm thinking there's most likely a bad noodle and there's current going back on the GEC what are your guys thoughts?

Sent from my SM-G986U using Tapatalk
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
I had a friend of mine call today he's a plumber.

He was using a metal snake and the snake hit the ground rod for the panel and he kept getting blasted

I'm thinking there's most likely a bad noodle and there's current going back on the GEC what are your guys thoughts?

Sent from my SM-G986U using Tapatalk
If I were a bettin man I’d say so...
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I would also measure for voltage between points that should be bonded, like from the neutral to water pipe, to rods, etc.

The panel may simply be missing its bonding screw. And, ask if they've had flickering light and premature bulb burn-outs.
 