Water Heater Continuity

Status
Not open for further replies.

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
While hooking up an electric water heater I checked continuity between the ground screw and the power leads to the heating elements. I was surprised there was continuity between the ground and both leads. When I turned on the breaker everything worked. I expected the breaker to trip. Any help understanding this?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I suspect you were getting a reading thru the equipment grounding conductor hooked in the panel. If you disconnect the equipment grounding conductor I would bet the reading would disappear.
 

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
I suspect you were getting a reading thru the equipment grounding conductor hooked in the panel. If you disconnect the equipment grounding conductor I would bet the reading would disappear.
Yes, you are correct. I did not disconnect the equipment ground from the tank.
 

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
Yes, you are correct. I did not disconnect the equipment ground from the tank.
Actually!! Now that I think about it I tested continuity between the ground screw and the NM conductors--no continuity.

I checked continuity with a simple continuity tool that sounds when the circuit is completed.
 