1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
If the Driven Ground conductor max size is #6, what size is used for the Water Ground, within 5 feet of the entrance to the dwelling?

If different what is the reference?

Norb
 

bphgravity

Senior Member
Location
Florida
Re: Water Ground

Grounding electrode conductors are sized from Table 250.66.

Only rod, plate, pipe, concrete-encased, and ground ring electrode conductors have a maximum required size. All the other permitted electrodes should be size from the table, including water pipes.
 

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
Re: Water Ground

I thought I would use 250.66. I have a garage, detached, with a new underground 200 amp service from the pad. There will be NO water available. What is the most widely accepted method to ground this type of installation?

Norb
 

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
Re: Water Ground

Bryan:

250.52(A)(5) Rod & Pipe Electrodes. I have been using Copper Ground Rods (5/8") with #6 as Driven Grounds.

Do I read this correctly that I can use this Cu rod buried 30" deep horizontally and then use #4 for the Conductor as the sole Grounding System?

Norb
 

bphgravity

Senior Member
Location
Florida
Re: Water Ground

CU ground rods are permitted to be 1/2 in. 5/8 are more than adequate.

You technically can't just arbitarily bury a ground rod 30 in deep without first trying to drive the rods vertically, and then at angles up to 45 degrees. See section 250.53(G)

A #6 is still the maximum required electrode conductor required to a ground rod whether its driven or buried.
 

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
Re: Water Ground

Bryan:

The installation is in an area where I KNOW that rock bottom is less that 8'. I hate to beat a dead horse but I'm trying to do a correct, safe, installation. Even though the service feeder is rated for 200 amps, 1/0CU or 4/0AL, and Table 250.66 lists the GEC as #4, with the grounding system only consisting of the driven, buried, then #6 is all I HAVE to use?

Thanks for working with me on this.

Norb
 

bphgravity

Senior Member
Location
Florida
Re: Water Ground

That's fine then. Here in coastal Florida, all you have to do is hit a ground rod about three times to get it 8' down! Obviously, the known geography of the area will dictate how installations will be made.

Yes, a #6 GEC to a ground rod is the maximum size required no matter what the size of the service entrance. You can run a #4 or larger to a ground rod, but it will not be any more effective than the #6.
 

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
Re: Water Ground

Bryan:

I'm sorry it has taken me so long to get back with you to thank you for your time and expertise. The information you provided has helped me understand this somewhat confusing situation.

Again, thank you.

Norb
 

bphgravity

Senior Member
Location
Florida
Re: Water Ground

No problem Norb. I'm glad I could help.

Click on the search function above, put in a topic, and you will find endless information. Feel free to post any questions you have, and post answers to other's questions.

Welcome to the Forum!
 