Checking to see if any one knows volt drop for #10 at 30 amps under a load lenght of wire etc. This is a r.v. park built in 70.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: voltage drop?

Darryl,

VD=

2 x K x D x I
______________
CM


K as far as generaly speaking would be 12.9 for copper.

D is distance

I is amps

CM is circular mill (Table 8 page 625 2002 NEC)

If you are dealing with three phase change the 2 to 1.732