Re: voltage drop?
Darryl,
VD=
2 x K x D x I
______________
CM
K as far as generaly speaking would be 12.9 for copper.
D is distance
I is amps
CM is circular mill (Table 8 page 625 2002 NEC)
If you are dealing with three phase change the 2 to 1.732
Roger