You can always add inter-lock contacts at the service switch to open the

vfd side at the same time, in case of accidental opening of service switch.

It's far less expensive in the long run.
 

charlie tuna

Senior Member
Location
Florida
i'll throw a wrench into the gearbox ------ how do you get around exceeding the voltage rating of the disconnect switch??? the output of the drive is above 600 volts!!!!!!!!!!!!!!!!!!!
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
charlie tuna said:
i'll throw a wrench into the gearbox ------ how do you get around exceeding the voltage rating of the disconnect switch??? the output of the drive is above 600 volts!!!!!!!!!!!!!!!!!!!

how do you get around exceeding the voltage rating of the motor and wiring?

The answer is they are rated in volts RMS I guess.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
benaround said:
You can always add inter-lock contacts at the service switch to open the

vfd side at the same time, in case of accidental opening of service switch.

It's far less expensive in the long run.


I have always specified a disconnect switch with an extra "early break" contact. Wire this contact to the VFD enable input, and when someone starts to open the disconnect, it shuts off the VFD before the disconnect actually opens.

Mennekes has an option for this on some disconnects: http://www.mennekes.com/products/disconnect/ms.html
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Charlie,
i'll throw a wrench into the gearbox ------ how do you get around exceeding the voltage rating of the disconnect switch??? the output of the drive is above 600 volts!!!!!!!!!!!!!!!!!!!
If that is correct than how can we use standard 480 volt motors and standard 600 volt wire?
Don
 

benaround

Senior Member
Location
Arizona
Steve66,

You would be surprized at how many guys don't spec. that in. Also, most

manafacturers instructions included with the vfd will spec. that in their booklet.

thanks for the link,
 