Hi folks, my jurisdiction is now on NEC 2020 and one of the curious changes is in article 690.45. Previously in NEC 2017 this article allowed you to forgo upsizing PV source and PV output circuit EGCs if you upsized ungrounded conductors for voltage drop (something 250.122 requires of all other EGCs). In NEC 2020 this articles changes it to all PV system circuits.
I heard that the rational for forgoing this upsizing in 2017 NEC was because the DC ground fault detector would work even if the impedence of the EGC system was higher than normal. If that is true then why would NEC 2020 allow this "exemption" for AC side circuits that don't have the same ground fault protection?
Also it leaves me confused about what to do with the AC grounded conductor (neutral). Since the PV system is balanced I typically size my grounded conductor to the smallest it can be. This is driven by article 250.24(C) which lets us size the grounded conductor according to table 250.122. So if I read that literally I would need to upsize that grounded conductor for voltage drop even though I am not upsizing my EGC due to the "exemption" in 690.45 (which only specifies EGCs not grounded conductors as well).
Does anyone have any thoughts of clarity or notice any holes in what I wrote? I'm leaning towards just upsizing due to VD on the AC side like I have been to play it safe but if anyone can instill some confidence in me it would be great not to use all that AL.
thanks,
I heard that the rational for forgoing this upsizing in 2017 NEC was because the DC ground fault detector would work even if the impedence of the EGC system was higher than normal. If that is true then why would NEC 2020 allow this "exemption" for AC side circuits that don't have the same ground fault protection?
Also it leaves me confused about what to do with the AC grounded conductor (neutral). Since the PV system is balanced I typically size my grounded conductor to the smallest it can be. This is driven by article 250.24(C) which lets us size the grounded conductor according to table 250.122. So if I read that literally I would need to upsize that grounded conductor for voltage drop even though I am not upsizing my EGC due to the "exemption" in 690.45 (which only specifies EGCs not grounded conductors as well).
Does anyone have any thoughts of clarity or notice any holes in what I wrote? I'm leaning towards just upsizing due to VD on the AC side like I have been to play it safe but if anyone can instill some confidence in me it would be great not to use all that AL.
thanks,