unbalanced load calc for 3 phase delta system

Status
Not open for further replies.

rnolan

Member
I have a 120/240 3 phase, 4 wire (center tap) delta system (B stinger). My 3 phase load is 80 kva per phase (A, B, and C). My single phase load is 34 kva phase A and 41 kva phase C. What are the amps for each phase and how is this calculated? What size (amp rating) panel is needed?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: unbalanced load calc for 3 phase delta system

Is this an exam question or a real situation?

How about you giving it a shot first, and showing us your results? It would help us to help you if we knew what parts of this process you already understood, and if we could see where you might be going wrong.
 

add

Member
Re: unbalanced load calc for 3 phase delta system

Originally posted by rnolan:
I have a 120/240 3 phase, 4 wire (center tap) delta system (B stinger). My 3 phase load is 80 kva per phase (A, B, and C). My single phase load is 34 kva phase A and 41 kva phase C. What are the amps for each phase and how is this calculated? What size (amp rating) panel is needed?
 

add

Member
Re: unbalanced load calc for 3 phase delta system

Originally posted by rnolan:
I have a 120/240 3 phase, 4 wire (center tap) delta system (B stinger). My 3 phase load is 80 kva per phase (A, B, and C). My single phase load is 34 kva phase A and 41 kva phase C. What are the amps for each phase and how is this calculated? What size (amp rating) panel is needed?
I recently had a test question similar to this. I have been tying to find study info on calcs for delta sevices and so far I have not found any real good info. So if someone could go thru the steps involved here it would be greatly appreciated.
 

RUWired

Senior Member
Location
Pa.
Re: unbalanced load calc for 3 phase delta system

rnolan , since,i am new to this site,( and i have been really enjoying the reading) i'll take a shot at it.
First, the 3 phase mulitplier for 240 volt system is 415.(240x1.732),so Phase a-b-c will be 192-192-192.(80000/415).A phase single phase load(34000/120) would be 283.C phase load 41000/120 would be 341.So total a phase load would be 475,B phase 192, C phase 533. 125% of the largest load would be the minimum breaker size 666amps or the next higher 800amp.Hope this helps,or gets you close.
Rick
 

rattus

Senior Member
Re: unbalanced load calc for 3 phase delta system

RUWIRED,

I see this problem a bit differently. The phase voltage in this delta system is 240V. I don't see where you get 415.

That being the case, the application of a bit of trig to the problem yields 577A, 700A, and 759A for the line currents. I have assumed that all loads present the same PF to make life easier.

Oops! Only the 577A is right. I will come up with the correct numbers manana.

Rattus

[ February 05, 2006, 11:56 PM: Message edited by: rattus ]
 

bob

Senior Member
Location
Alabama
Re: unbalanced load calc for 3 phase delta system

I see this problem a bit differently. The phase voltage in this delta system is 240V. I don't see where you get 415.
He is using a multipler of 240 x 1.73 = 415.
80000/415 = 192 amps per phase. I don't see how you arrived at your figures.

Edit
I read the post again. I thought it was 80 kw total. 3 x 80 = 240 kw/.415 = 578 amps per phase.

[ February 06, 2006, 11:36 AM: Message edited by: bob ]
 

spsnyder

Senior Member
Re: unbalanced load calc for 3 phase delta system

All the figures are given on a per phase basis. If you use 240V to calc. line current you have to multiply the Apparent Power by 3.

I get the following.

A = 80 kVA = 577.4 Amps
B = 34 kVA = 283 + 577.4 = 860.6 Amps
c = 41 kVA = 341 + 577.4 = 919 Amps.

[ February 06, 2006, 11:33 AM: Message edited by: spsnyder ]
 

eeee

Senior Member
Re: unbalanced load calc for 3 phase delta system

Don't believe you add individual single phase KVAs to each phase of the 3 phase KVA. I believe you add all KVAs for each item (3 phase and single phase), then calculate current for design load from total KVA.

Not sure about the issue with the trig for the delta.
 

rattus

Senior Member
Re: unbalanced load calc for 3 phase delta system

It is like this gents,

The phase currents in windings AB and BC are

80KVA/240V = 333A.

These currents combine to yield,

Ib = 333Ax1.732 = 577A

For winding CA, 68KVA of the single phase load may be treated as a 240V load and added to the 80KVA load to yield 148KVA of 240V load. Load (not line) current is 148KVA/240 = 616A. To obtain the line current, Ia, we combine vectorially the phase current from winding AB.

Ia = 616A + 333A[cos(60) +jsin(60)] = 783A + j289A yields 835A magnitude.

The remaining 7KVA of single phase load adds 58.3A into node C. Then

Ic = 616A + 58.3A + 333A[cos(60) +jsin(60)] = 841A + j289A yields 890A magnitude.

Phase currents cannot be added algebraically since their phase angles are different. The standard formulas do not work because the imbalance is so great. This is not a simple problem.

Anyone see it differently?

Edited to correct errors.

Rattus

[ February 08, 2006, 11:51 AM: Message edited by: rattus ]
 

eeee

Senior Member
Re: unbalanced load calc for 3 phase delta system

Rattus,

"The remaining 8KVA of single phase load"

41KVA-34KVA=7KVA. I would think you should have stated the reamining 7KVA of single phase load and this would change your numbers some.

Interesting with the delta the way the phase, line and load currents are calculated.
 

rattus

Senior Member
Re: unbalanced load calc for 3 phase delta system

eeee

I did that on purpose--believe that?

I have corrected the first post.

Rattus
 

Zifkwong

Member
Re: unbalanced load calc for 3 phase delta system

I am getting

Ia = 835 A
Ib = 890 A
Ic = 577 A

I added them vectorially, if that is a word. For B phase I had 333.33 Amps + 341.667 Amps at an angle of 0 and 333.33 Amps at an angle of 120.
For A phase I had 333.33 Amps + 283 Amps at an angle of 0 and 333.33 Amps at an angle of -120.

Am I confused?
 

rattus

Senior Member
Re: unbalanced load calc for 3 phase delta system

Zif,

You are not confused; you are right! I treated 34KVA as 240V load; I should have treated 68KVA as 240V load. That is what I get for trying to be fancy!

Rattus
 

RUWired

Senior Member
Location
Pa.
Re: unbalanced load calc for 3 phase delta system

ok, i reworked the math due to thinking single phase loads were 120 volt.

80000/415=192 a-b-c
34000/240=141 a-c
7000/120=58 c-n
Total-A=333
Total-B=391
Total-C=192
Total-N=177
391/.8=488 next higher 600amp main breaker
Rick
 

bob

Senior Member
Location
Alabama
Re: unbalanced load calc for 3 phase delta system

ok, i reworked the math due to thinking single phase loads were 120 volt.
80000/415=192 a-b-c
RU
You are making the mistake I made. The 3 phase load is 80 kw per phase or 240 kw.
You can just add the amp load. Look at the way Rattus has it caculated.
 

rattus

Senior Member
Re: unbalanced load calc for 3 phase delta system

Originally posted by RUWired:
ok, i reworked the math due to thinking single phase loads were 120 volt.

80000/415=192 a-b-c
34000/240=141 a-c
7000/120=58 c-n
Total-A=333
Total-B=391
Total-C=192
Total-N=177
391/.8=488 next higher 600amp main breaker
Rick
There is no way to get 415V from a 240V delta. The balanced phase currents are,

80KVA/240V = 333A

Add these vectorially to obtain the line current,

Ib = 333Ax1.732 = 577A

Now figure the "phase" currents at A and B:

Ian = 34KVA/120V + 333A = 616A (algebraic)

Ibn = 41KVA/120V + 333A = 675A (algebraic)

Now add vectorially the 333A phase currents from the other windings to obtain,

Ia = 835A

Ib = 890A

Now if we had only the 120V loads on ANC, we would have a quite different problem.
 

RUWired

Senior Member
Location
Pa.
Re: unbalanced load calc for 3 phase delta system

Bob, If i have a 3 phase load drawing 80 kva, i don't say i have a 240kva load, i say i have an 80kva load. amperage is based on 80kva / by voltage-phase at hand. in this case it is 240 3 phase and the multiplier is 415. If i have a 192 amp 240v 3 phase load and want to find kva, i multiply 192x415= 79680kva(80).
Rick
 

RUWired

Senior Member
Location
Pa.
Re: unbalanced load calc for 3 phase delta system

rattus,E-L=E-Px1.732
Line voltage =Phase voltage x 1.732
Rick
 

RUWired

Senior Member
Location
Pa.
Re: unbalanced load calc for 3 phase delta system

Hey Rattus, I don't understand/learned vectors.I never got into that end of the math.It took a while to understand apparent power.
Rick
 