Can't you get 25kVA of 120V (or 208A) from a single 1ph 25kVA xfmr LV side, but to get the same 208A/25kVA/120V from a 240/120V high leg setup 3ph xfmr, you'd need a 75kVA xfmr, as it's only using 1 of the 3 windings?
I agree with the other posters here in that your lack of understanding of the fundamentals and your misuse of the terminology are real problems. I appreciate your curiosity and willingness to learn, but wwhitney and others have given excellent examples and explanations, which you seem to ignore. Focusing on the kva rating of the poco transformer is a waste of time for conventional power flow. (I grant that in PV applications it can matter.)
Thanks for the comment. Could you please explain how I misused terms in the comment above?
It seems like I'm using different terms to describe the same thing as other people, but they don't quite like it.
I understand your example with the house. The point I'm trying to get across is that yep, that's the way standard *residential* services work, but when you get into service upgrades, the POCO asks you to fill out the load sheet so they can size the xfmr accurately (whatever size that may be)
That's all.
About my quote above:
Let's forget about POCOs and PV for a minute. There's a 480V delta service and 480V delta inverters, amps of both are "more than enough".
So a new building goes up and the owner of the property and PV wants to power it.
It's a storage barn and the total equip. load in the building is eight 120V fans, 25A each.
That's 24kW of load.
You could supply that load from:
A. A single 480V to 120V 1ph transformer connected to 480V L1 and L2 to the xfmr H1 and H2, load connected to xfmr X1 (L1) and X2 (neutral/bonded to load panel).
or
B. A single 3 phase 480V delta to 240V delta/120V center tapped xfmr.
Xfmr A would be 25kVA. Xfmr B would have to be 75kVA.
Is that ok so far?