ryan_618
Senior Member
- Location
- Salt Lake City, Utah
I just recieved an E-mail regarding the 2005 version of 680.26(C). I have called the authors of this to verify that what they got is a "formal interpretation" or just a chat with someone t=from NFPA. I left a message, and will post to this thread when I hear back. Anyway, here is the message I got:
Date: April 6, 2005
To: Our Valued Customers
Re: 2005 National Electric Code (NEC)
In February 2005, Latham International discovered the NEC Handbook interpretation of article 680.26(C) of the 2005 NEC requires the installation of an ?equipotential bonding grid? under the deck and bottom contour of vinyl lined polymer wall pools. Latham and a growing number of customers quickly became concerned with the added cost of installing a bonding grid with each pool.
After reviewing the code itself, we believe the wording to be ambiguous and the bonding grid is required only under the deck, not the entire pool bottom contour. There is no sound technical rationale for having a bonding grid under a non-conductive pool bottom. However, a wet pool deck (concrete, stone, or pavers) will act as a conductor and should be bonded to the grounding system.
At the February 22nd APSP Technical Committee meeting, Latham and the APSP challenged the requirement with a request for a Formal Interpretation to the National Fire Protection Association (NFPA). The NFPA is the author of the NEC.
On March 18th, the NFPA reviewed our request. The discussion was in our favor and the code wording does not represent the intent of the revisions for 2005. The intent was to require a bonding grid only under the deck (for vinyl lined polymer wall pools). Given that the published change has resulted in an adverse impact and was inadvertently overlooked, the situation qualifies for a Tentative Interim Amendment (TIA). A TIA is a revision to the code allowed in emergency situations.
Unfortunately, the TIA process takes several months and the projected effective date is August 15th. Since the situation is urgent and our customers cannot wait until August, we are seeking immediate alternatives.
Similar to ANSI standards, adopting the revision is discretionary. Some municipalities have the option of postponing the effective date of article 680.26(C). In fact, Columbus Ohio recently set a precedent by becoming the first municipality to delay adopting 680.26(C) until after the TIA process or September 1st.
The APSP has also contacted the International Association of Electrical Inspectors (IAEI) to discuss alternatives. Latham will continue to work with the APSP, NFPA, and IAEI until an amicable solution is obtained. If you have questions, please contact either Peter Moran or Don Nicoll at (800)833-3800. Thank you.