The differenece ground wires

Status
Not open for further replies.

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Re: The differenece ground wires

One is stranded the other is solid :)

I believe the NEC requires #6 and larger to be stranded though we do have a coil of #6 solid TW insulated (in telephone gray I might add) ground wire that we use to ground TELCO protectors and equipment.

-Hal
 

hurk27

Senior Member
Re: The differenece ground wires

I believe the NEC requires #6 and larger to be stranded
I have never heard of this requirement?

250.62 allows both with no restriction on size for grounding electrode conductor.

250.118(1) allows both with no size restriction for equipment grounding conductor.
 

bphgravity

Senior Member
Location
Florida
Re: The differenece ground wires

Section 310.3 states, "where installed in raceways, conductors of size 8 AWG and larger shall be stranded."

The Exception then states, "as permitted or required eleswhere in this code".

Grounding conductors would be one of those exceptions.

[ October 25, 2004, 10:32 AM: Message edited by: bphgravity ]
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Re: The differenece ground wires

Yup, that's what I was thinking of. If I had gotten up off my butt and looked in the book I could have quoted it correctly! :eek:

-Hal
 

pierre

Senior Member
Re: The differenece ground wires

"As permitted or required elsewhere in this code" - one example is solid 8 AWG used in raceways for pools, as we us a lot of solid 8 AWG, so they relax the Chapter 3 requirement somewhat.

Pierre
 