Table 310-16

Status
Not open for further replies.

buck

Member
Location
California
Have often heard that figuring wire size from table 310-16 is based on 60 dgree column for wire size #1cu and below.I can't seem to find a reference to this,any help? Thanks in advance
 

bob

Senior Member
Location
Alabama
Re: Table 310-16

Buck read that entire section Ron has listed. If the terminals are rated foir 75 degrees you can use the 75 degree col for any conductor.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Table 310-16

Originally posted by bob:
If the terminals are rated for 75 degrees you can use the 75 degree col for any conductor.
Any conductor rated at least 75 C.

Not NM (334.80), UF, TW etc.

However when adjusting ampacity (derating) for temp or number of conductors you can use the 90 C column. ;)
 

ccha9219

Senior Member
Re: Table 310-16

A a rule use the 75 degree chart. There is no such thing a a 90 degree rated lug, (Or at least not that I have seen)As iwire said execpt for derating.
 

buck

Member
Location
California
Re: Table 310-16

Thanks guys,appreciate the response.I must've been thinking of NM but that was cleared up by your responses.
Thanks again
 

rb

Member
Location
Tennessee
Re: Table 310-16

Be careful Buck. The entire assembly must have 75 degree terminals. The circuit breaker and panelboard may be rated for 75 degrees but the receptacle or utilization equipment may have 60 degree terminals. Whichever is lowest will prevail.
 