Please help me determine if there is a code violation.
UL 1558 listed Switchgear rated at 4000A.
At its worst case, which will probably never be reached, continuous load provided by several 100% rated feeder breakers totals 3,900A.
Switchgear is listed as 100% rated per the UL Listing and the breakers seem ok per the exception for 215.2(A)(1).
What do you think?