templdl said:
As I understand it electrical equipment that contained breakers that could be withdrawn form their enclosure by means of a rack and pinion type gear mechanism was said to be switchgear.
It is common for both low and medium voltage enclosed breaker enclosure lineups to allow the removal and installation of breakers in a similar fashion to be refered to as switchgear.
Today the term switchgear appears to include any electrical equipment that is made up of floor standing enclosures.
No.
Within the moniker "switchgear", there is Metal-Clad draw-out switchgear, which is what you just described, and there is also Metal Enclosed Interrupter Switchgear (MEIS), which is NOT draw-out.
Switchgear = Individual switching devices in a lineup, sometimes can include only 1 device in the "lineup", sometimes there are versions with special "2-high" units. Can be circuit breakers, vacuum breakers, fused switches, even motor controllers. The operative issue is no matter what the design, each switch unit is fully isolated from any other one by metal barriers, so if a fault happens in one circuit, the damage does not spread to other units.
Switchboard = a group of switches all in the same cabinet, no isolation in between devices. Usually involves fused switches as opposed to circuit breakers. Less expensive than Switchgear, but runs the risk that a fault in one device will take down the entire system. Some people opt for this because everything in the system is interdependent anyway, but this is being used less and less, especially with the new Arc-Flash safety requirements. I see the day when switchboards will be no more.
Panelboard = a grouping of molded case or insulated case circuit breakers. Same as a switchboard concept but because each breaker is in its own case, fault management is easier. Usually refers to Low Voltage (600V and under) only.
Load Center = el-cheap-o version of a panelboard typically foound in residential applications where cost is king. Fault management by virtue of containment of the flames to within the box, but newer cheaper "home-line" versions are coming out with plastic boxes, so even that may be going by the wayside..