Switch ampacity question

Status
Not open for further replies.
Location
New York
Occupation
Electrical apprentice
Is there anywhere in the code that illicitly says it’s acceptable to use a larger switch than ckt rating on a circuit? Ex. Using 20 amp toggle switches throughout a house on 15 amp lighting ckts

It’s done pretty commonly with disconnect switches being rated for up to 60 amps being used on a 20 amp circuit let’s say

I know to never go the other way of course with let’s say 15 switches than on a 20 amp rated ckt although some argue it’s fine, but does anyone have a reason or code section that says to not use larger switches than circuit rating? As far as I know it’s just like using larger wire than needed on a ckt but could be wrong
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
I can't think of anything prohibiting it,
but I can think of a few scenarios where a switch larger than the circuit would be a necessity.

You mentioned a 60 amp disconnect on a 20 amp circuit, But even more common would be a 60 amp disconnect (safety switch) on a 40 amp circuit. You certainly can't put that on the 30 amp disconnect, and have no options in between
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
If you go to _extreme_ aspects of this, you can encounter design problems (not code violations).

For example, if you use an oversized switch (say a 20A light switch) to control logic level signals (milli or micro amps at 5V) then you can have problems with insulating oxide layers forming on the contacts and the signal not being able to punch through them.

-Jon
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I know to never go the other way of course with let’s say 15 switches than on a 20 amp rated ckt although some argue it’s fine, but does anyone have a reason or code section that says to not use larger switches than circuit rating? As far as I know it’s just like using larger wire than needed on a ckt but could be wrong
A 15 amp snap switch is permitted on a 20 amp circuit as long as the connected load on the switch doesn't exceed its rating. Similar to 600 watt rated dimmers used on 15 and 20 amp circuits.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
If you go to _extreme_ aspects of this, you can encounter design problems (not code violations).

For example, if you use an oversized switch (say a 20A light switch) to control logic level signals (milli or micro amps at 5V) then you can have problems with insulating oxide layers forming on the contacts and the signal not being able to punch through them.

-Jon
Indeed. See this sometimes with switches used on fireplace power pile circuits.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
But even more common would be a 60 amp disconnect (safety switch) on a 40 amp circuit. You certainly can't put that on the 30 amp disconnect, and have no options in between
What about a 40A circuit for a 5HP, 208V, 3ph motor? I can't see any reason the motor disconnecting means couldn't be a 30A disconnect.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
That wouldn't be a 40 amp circuit. That would be a 20 amp circuit.
How would a circuit with a 40A OCPD be a 20A circuit?

Instead...A 40A branch circuit supplying two 3000W, 240V single phase water heaters. With separate 30A disconnect switches at each water heater.
 
Location
New York
Occupation
Electrical apprentice
A 15 amp snap switch is permitted on a 20 amp circuit as long as the connected load on the switch doesn't exceed its rating. Similar to 600 watt rated dimmers used on 15 and 20 amp circuits.
Right I’ve seen that code. Was more curious about using a 20 amp switch on a 15 amp ckt, logic says go for it because it’s rated for 20 amps so it can handle 15 amps through it. I just like to see it in the code as acceptable but don’t see anything about using larger switches or wire for that matter in the code
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I just like to see it in the code as acceptable but don’t see anything about using larger switches or wire for that matter in the code
Positive wording as you've suggested is not necessary because these things are written as the minimum standard. Besides electrically what would be the downside of using a 20 amp rated switch on a 15 amp circuit? 20 amps is the maximum rating.
 
Location
New York
Occupation
Electrical apprentice
Positive wording as you've suggested is not necessary because these things are written as the minimum standard. Besides electrically what would be the downside of using a 20 amp rated switch on a 15 amp circuit? 20 amps is the maximum rating.
I don’t suppose any besides a couple of bucks. Just was taught to match ckt size to proper size wire, devices but no harm in my eyes using em if you have them. Larger wire in the middle of a circuit just cause you have it is a bit risky though
 
Location
New York
Occupation
Electrical apprentice
I don’t suppose any besides a couple of bucks. Just was taught to match ckt size to proper size wire, devices but no harm in my eyes using em if you have them. Larger wire in the middle of a circuit just cause you have it is a bit risky though
IMO the wire range on the device tells you 14-10 awg so that tells you what’s acceptable
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Just was taught to match ckt size to proper size wire
That's not required either. Some think that it's a good practice but in the NEC doesn't care as long as the smallest section of the run has a conductor ampacity that is greater than or equal to the OCPD ahead of the circuit. Where voltage drop compensation has been applied you may see conductors several sizes larger than the minimum required for the circuit and that is perfectly normal. Motor and AC units would be another area where the OCPD is likely to be larger than the ampacity of the conductor.
 
Location
New York
Occupation
Electrical apprentice
That's not required either. Some think that it's a good practice but in the NEC doesn't care as long as the smallest section of the run has a conductor ampacity that is greater than or equal to the OCPD ahead of the circuit. Where voltage drop compensation has been applied you may see conductors several sizes larger than the minimum required for the circuit and that is perfectly normal. Motor and AC units would be another area where the OCPD is likely to be larger than the ampacity of the conductor.
Agreed!
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
Larger wire in the middle of a circuit just cause you have it is a bit risky though
Why? We do sort of thing that for voltage drop. As long as all the wire in the circuit has enough ampacity for the OCPD it can be as large as you like.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
There is no Code prohibition against using switches rated for MORE amps than necessary. Nor is there a technical reason to worry about it. The only affect it has is on the project cost.

On the side issue regarding disconnect switch sizes, it’s important to note that on motor circuits, the switch must bear a Hp rating equal to or greater than the motor it is feeding. Amp rating is less relevant and in fact is IRRELEVANT if there is a lower HP rating than you think it should be, which happens sometimes.
 