subpanel seperation

Status
Not open for further replies.

bond

Member
Maybe im too lazy but seeing you all probably know this I have to ask quick. Isnt there some sort of distance rule that when you install a sub panel so many limeted feet from the main breaker panel that you do not have to seperate the ground and neutral connections? thanks, is it in the code?
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: subpanel seperation

If a panel does not contain a service disconnecting means the neutrals and grounds must be separated. The only exception to this is a separate building or structure fed from a common service.

It is possible to have two or more service disconnecting means, a common example is two 200 amp main breaker panels fed from one meter.

In this case both panels contain service disconnects and both will have the the neutrals and equipment grounding conductors bonded.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: subpanel seperation

I agree with Bob. If there is a sub-panel that gets power from a main panel, the N and G are separated. Distance means nothing.
 

bphgravity

Senior Member
Location
Florida
Re: subpanel seperation

If the main panel feed to the sub panel is with a metallic raceway, what would be the point of separating the grounded and bondng conductors?
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: subpanel seperation

Originally posted by bphgravity:
If the main panel feed to the sub panel is with a metallic raceway, what would be the point of separating the grounded and bondng conductors?
If we bond at both ends of the raceway the raceway is a now a a neutral conductor. Any loose joints in the raceway could be a source of electrical shock or heating.
 

cripple

Senior Member
Re: subpanel seperation

The bonding the of the neutral conductor and the equipment grounding conductor is prohibited on load side of the of the service in Section 240.24 and only permitted in Section 250.32(D). By bonding the equipment grounding conductor to the neutral coductor as you asked would violate Section 250.6, 250.142, 300.3 and 310.4.

Some panelboards incorporate neutrals factory bonded to the frame or enclosure and are list and labeled ?Suitable Only For Use As Service Equipment, this permits the equipment grounding conductor to be terminated to the neutral buss per Section 250.142.

Other panelboard with the neutral buss isolated from the frame or enclosure will be list and labeled as Suitable For Use As Service Equipment, this type of panelboards will come with a bonding screw or strap which is supplied by the manufacture. This type of panel can be used as subpanels when feed from the service panel, without the use of the bonding jumper as required per Section 250.24(A)(5).
 

bphgravity

Senior Member
Location
Florida
Re: subpanel seperation

Originally posted by iwire:
If we bond at both ends of the raceway the raceway is a now a a neutral conductor. Any loose joints in the raceway could be a source of electrical shock or heating.
But isn't this what we do between a meter enclosure and a main serivce disconnect? Both enclosures are bonded to the service grounded conductor and a metallic raceway can be used between the two.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: subpanel seperation

Bryan,
But isn't this what we do between a meter enclosure and a main service disconnect? Both enclosures are bonded to the service grounded conductor and a metallic raceway can be used between the two.
For some unknown reason electricity knows if it is on the line or load side of the service disconnect and only chooses to cause problems with parallel grounded conductor paths on the load side of the service disconnect.
Don

[ October 12, 2004, 01:29 PM: Message edited by: don_resqcapt19 ]
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: subpanel seperation

Originally posted by bphgravity:
But isn't this what we do between a meter enclosure and a main service disconnect?
Yes of course, I am aware of that.

My question would be;

Why is double bonding allowed on the supply side?

Not why isn't double bonding allowed on the load side.

IMO both situations are potential trouble.

But I guess Don has explained the reason for the different rules. ;)

[ October 12, 2004, 01:42 PM: Message edited by: iwire ]
 

bphgravity

Senior Member
Location
Florida
Re: subpanel seperation

Originally posted by iwire:


My question would be;

Why is double bonding allowed on the supply side?

Not why isn't double bonding allowed on the load side.
Yes I agree, that is the better question. :eek:
 