sub feed or not

timmermeier

Member
Location
alton il
Occupation
electrician
I have a meter base with a 100 amp breaker feedthrough on outside of house . inside i have a 100 panel with main lugs . is this a subfeed
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Since the service disconnect is outside the conductors between it and the panel are feeders so it is therefore a "sub-panel".
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I have a meter base with a 100 amp breaker feedthrough on outside of house . inside i have a 100 panel with main lugs . is this a subfeed
Three or four conductors? Should be four, grounds and neutrals separate, no bonding jumper in sub-panel.
 