I have a meter base with a 100 amp breaker feedthrough on outside of house . inside i have a 100 panel with main lugs . is this a subfeed
Yes it is.I have a meter base with a 100 amp breaker feedthrough on outside of house . inside i have a 100 panel with main lugs . is this a subfeed
YES,Is the outside breaker the service disconnect?
Three or four conductors? Should be four, grounds and neutrals separate, no bonding jumper in sub-panel.I have a meter base with a 100 amp breaker feedthrough on outside of house . inside i have a 100 panel with main lugs . is this a subfeed