I have designed a partial fire alarm system consisting of smoke detectors, pull stations, horns and a strobe panel that will serve only 2 floors of a high rise building. This partial fire alarm system is connected to the building's main fire alarm system. On the drawings approved by FDNY, the power for the partial fire alarm system is tapped ahead of the main lugs of the nearest 120/208V panel. To my understanding, this is a common practice but I received letter of defect from FDNY specifying to "provide for power to be tied and fused in street side of electrical service prior to meter, transformer disconnect switch as per code". I was considering complying but that would require the contractor to run almost 300 ft run into a garage to achieve this. I am preparing to dispute the inspector's claim but I can not find in the code to support wiring connections for partial systems. Please help? Thank you