It can be done, but the issue is that you cannot backfeed a generator like you can the grid, so in an off grid situation when the PV output exceeds the load and the storage is full, you have to be able to either throttle back or turn off the PV. PowerWalls can munge the frequency of their inverters, and some inverters can recognize the change and throttle back accordingly.Pretty much other than I find many grid tie inverters to lack many features for generator support, priorities, etc. There are very few that will actually run a generator, sync to it, and use it only as a supplement to the solar when solar is made a priority.
I am open to hear from others here on options but consider you have a 5kw load, and running only a 2kw generator. If the inverter does it's job, it will pull 2kw from the generator and 3kw from the solar system for the load. Once things are well sustained, the generator can either push charging to a storage pack or just throttle back.
Generators are demand sources, so they do throttle their input back when demand is lower, but they cannot have a negative output. Maybe some commercial ones can, but regular consumer level generators can't. That's why a common solution is to interconnect the PV outside the ATS for a grid tied service with generator backup. Batteries are really not a player because the case where they are full (and therefore virtually not present) needs to be taken into account.