I have a dilemma with a Mitsubishi Split system. The nameplate says MOCPD is 50Amps and the minimum circuit ampacity is 28A... Currently fed with #10's, however being told I need #8's. Who's correct?
I have a dilemma with a Mitsubishi Split system. The nameplate says MOCPD is 50Amps and the minimum circuit ampacity is 28A... Currently fed with #10's, however being told I need #8's. Who's correct?
The inspector wanted to know if the minimum ampacity included the 125% motor rating as per NEC 440.32........
The MCA takes all of that, including multiple motors if applicable, into account.