@sketchy
Okay, there's a lot going on here and a lot already been said, so hopefully I'm not missing anything important...
Main points:
1) Since the bussing between each meter and breaker is not to be modified, I believe you must be talking about tapping the feeder for each unit on the load side of it's breaker. All further comments below are based on this assumption.
2) It matters a whole lot what code cycle you are on, regarding whether your AHJ should/will allow such load side taps, period. 2014 has clear rules which require either that the feeder is rated high enough for both sources, or that you install an overcurrent device downstream. See 705.12D(2). The 2011 code is highly ambiguous about such taps, since no rules are explictly written to address them. If on that cycle you should make no assumptions about your AHJ's allowing such taps at all (but also don't give up). Best case, with only 7amps on each PV system your feeders may already rated high enough for both sources. For example #2 Cu on 100A breakers would be just fine under 2014 and you'd have a solid case for convincing the AHJ under 2011.
3) Next we have the question of whether each unit's breaker is a service disconnecting means or not. It's paramount that this question be clear between you and the AHJ. If each unit's breaker is a service disconnecting means, and they allow the load side taps, then we are all good if the taps are allowed. However if another disconnect upstream of the meters is considered the service disconnect, and the AHJ considers the meterbank a panelboard, then this is totally uncharted territory for me personally. Again, it matters hugely what code cycle you are on. 2014 has more different rules and options for ratings of panelboards, and 705.12(D)(3)(C) could probably give you the permission you need. 2011, on the other hand, could put the kabosh on the entire project, since all your sources couldn't be installed on the 'opposite end' if you're invoking the 120% rule.
In conclusion, there's a lot of ambiguity here that could really screw up this whole project if your AHJ doesn't understand/agree with what you're doing. You'd better be real clear with them in your proposals and how you're interpreting each code section that could bear on the subject.