espo229
Member
- Location
- New Jersey
Just started doing these 50 amp heated spa units.I dont have any problems till I get out to gfci enclosure.I am tired of reading art.680 so am asking for input. Art. 680 42a1 says no more than 6 ft. of flex to unit. If I mount gfci 5ft. away, 3 to 4 ft.up the wall and add 1ft.the spa is supposed to be away from the house and then find out the control box is on the other side, I could be looking at 12 to 15 ft.of flex both inside and out of the unit. Both of the spas Im doing are in corners of homes that form 90s and on slabs. Will call for inspection this week and see what ahj says. If this was a pool, no problem. But these spas are being dropped down in some strange places.